Jump to content

Fitting my own house vent(s) in preparation for a Fosse toutes Eaux to be installed.


Howie
 Share

Recommended Posts

I know what I would do in the UK, - where there are no inspections or regulations (to speak of). However, I am about to install my fosse vents into an old stone longere ready for a professional Fosse Toutes Eaux installation.

But do I really have to have two totally separate vent runs; one from the internal pipe which feeds all waste to the tank, and one from between the tank and the soakaway? Or is it possible to amalgamate these into one, so that I only have to have one vent running up through the house and one vent outlet sticking out through the roof?

Also, I am hoping that it is possible to get a 100mm to box-section conversion for the vent/s because I want to run it under my ceiling, - above the perlings. So, any advice on which products to buy would be gratefully received!

Thanks in advance.

Howard.

Link to comment
Share on other sites

My house is 100 years old and has had various generations of plumbing installed over the years

My new Fosse Toutes eaux which was professionally installed a few years ago and recently inspected -and passed - by SPENC (?) has but the one vent pipe which runs, as you indicate, from the fosse. This travels up the outside corner of the house to a little above the guttering.  The only other connection which isn't delivering water, is an air admittance valve which stops the flow from the kitchen pulling the water out of the bathroom traps.

I noticed in the bathroom of a friend's new house that he has a 100mm pipe running up the corner of the room 'T'-ed - one assumes - from the soil pipe. Since this doesn't appear out of his roof, I can only assume it's also an air admittance pipe, in which case 100mm is more than a little excessive. 50mm would do fine. 

I've no doubt there will be alternative views....!

p

Link to comment
Share on other sites

I have just completed a job where, apart from the fosse vent, SPANC aka Viola insisted on a 100dia vent off every toilet in the building

This included a ground floor toilet which only had a short drain run prior to connecting to the drain close to the fosse vent

Not necessary but he would not sign off the installation without the vents so I had to install them

I suggest you get your fosse installer to talk to SPANC and clearly establish what they require for ventilation in the property before you go too far

The problem is most of the inspectors are young lads, not plumbers, who have been trained on the rule book and really know nothing about wastes and drainage

Le Plombier

Link to comment
Share on other sites

We are on mains drains and the wastes are run in 100mm grey plastic however no vents at all yet there are sinks etc bossed into the line. I had intended to rip this lot out and introduce a conventinal (UK style) SVP arrangement having looked at neighbouring houses it seems the French don't go much on air admittance?

Link to comment
Share on other sites

Big Mac

They do now under the tout eau regs for fosse installations

In reality all you need is a vent at the head of the drain at 100mm dia and anti siphon pipes at a reduced diameter where applicable

With new fosses they seem to be insisting on a 100mm vent up to roof level from every single toilet in the building

The example I referred to in my previous posting was a complete new plumbing installation where no bathrooms previously existed

Even the fosse installer argued with SPANC over the ruling but to no avail

A new fosse and connection to existing may well mean they will inspect the fosse only and not the existing internal installation, who knows?

Best to ask them to be sure

My own installation, quite old,  has only recently been inspected by SPANC

It does not comply but due to the property and land layout they have said there is probably not much you could do to change it

Their survey shows no vents, not even a fosse vent and there is no adverse comment about this on the report even though the lack of a fosse vent is a non compliance

It just depends how lucky or unlucky you are with the inspector you get

I know with my gas audits the inspectors do know the regs and interpret them correctly and very strictly but with SPANC it seems to be a lottery

Le Plombier

Link to comment
Share on other sites

Well, thanks so much for the advice everyone. I think I will put a 100mm vent/soil pipe through the roof (as long as I can get a box-section conversion for the ceiling part) and that will then be my main pipe out of the house. Luckily, there is only one toilet. I suppose I could also run a 40mm pipe alongside it and that will be the vent from the fosse side. If I run it up from the fosse pipe and link it back into the 100mm vent above all waste runs, that should take care of any possible air inlet and vent problems.

Even that all seems like overkill to me. However, if the SPANC inspector wants another 100mm vent for some reason, I will just take it up the end gable outside the property with no more disruption inside the house. Of course, I will be very tempted to remove it again, - after he has approved the installation!  [;-)]

 

Link to comment
Share on other sites

On the installation I referred to all vents ( 1 fosse and 2 wc ) had to be run separately in 100mm dia to the roof

He would under no circumstances allow a smaller size or for the vents to be joined at any point

He did return for a final inspection after the work was complete

Le Plombier

Link to comment
Share on other sites

Laughing at myself here because I intend to put 2 other bathrooms in one obove the other (3 Storey arrangement as only bathroom is currently effectively in the cave) Do I really need to drop 2 stacks from above to chamber then introduce a vent from existing so in effect 3 vents externally (Hammond organ anyone)?

A nice SVP With a DURGO on WC branches was my intention although I may run 'Foul'! of some spill over regs for DURGO location maybe?

I love France!

 

Link to comment
Share on other sites

[quote user="Howie"]I know what I would do in the UK, - where there are no inspections or regulations (to speak of). However, I am about to install my fosse vents into an old stone longere ready for a professional Fosse Toutes Eaux installation.

But do I really have to have two totally separate vent runs; one from the internal pipe which feeds all waste to the tank, and one from between the tank and the soakaway? Or is it possible to amalgamate these into one, so that I only have to have one vent running up through the house and one vent outlet sticking out through the roof?

Also, I am hoping that it is possible to get a 100mm to box-section conversion for the vent/s because I want to run it under my ceiling, - above the perlings. So, any advice on which products to buy would be gratefully received!

Thanks in advance.

Howard.

[/quote]

 hi ok

  The answer is no , the 110 mm soil pipe going into the fosse has a  90 degree bend on it and 1 meter of pipe going into the tank so you cannot use it as a vent ,

 the vent pipe for the fosse is situated 100mm above the fluid level of the tank to..... vent the tank  ... this is normaly on the inlet side anyway so if yours is on the outlet ...mmmm you could have the tank in the wrong way round

  look here

you can see the in let and the vent is 4" higher

               Dave

image link repaired by a mod

Link to comment
Share on other sites

Hi again. Thanks for that. No, - maybe I wasn't very clear. I was meaning the ventilation secondaire as shown HERE

Now, I would think that it makes sense to make the primary ventilation outlet as high as the height shown in the diagram for the secondary vent. Then, bring the secondary vent out of the ground as a 40mm pipe, run it up, - parallel with the primary pipe, right inside the house until it reaches a height which is above all waste connections (just air). Then tap it into the 100mm pipe. Hey presto: Only one protruding vent!

I'm sure it doesn't comply, but I can't think why and it makes perfect sense.

No?

Link to comment
Share on other sites

hi ok

               the systems are both the same ,the one that you show is the way it`s done with concrete tanks

 this is taken from the S.V.L web site

VENTS

Two vents are always required and these are the most important part of the installation if odours are to be avoided. Both vents must be taken above the property roof eaves levels

Primary vent - 100 mm and taken from the downpipe from the WC straight up through the roof

Secondary vent - 100mm and taken from the top of the fosse outlet pipe, back to the property and then up an outside wall - can be taken through or outside the roof tiling.

   but they will let you fit a durgo valve to the primary

              Dave

Link to comment
Share on other sites

[quote user="DaveandOlive"]

hi ok

               the systems are both the same ,the one that you show is the way it`s done with concrete tanks

 this is taken from the S.V.L web site

<snipped vents quote>

   but they will let you fit a durgo valve to the primary

              Dave

[/quote]

Thanks for the info Dave. It's a damn nuisance really, but I'm not shooting the messenger!

My longere has 6 velux windows and they effectively make up the top floor of the house. So I'm guessing that both vents will have to be higher than those. Routing two 100mm pipes through the floors and then through a slate roof is not just awkward, - it's downright unsightly. (This is only a small house).

I know there's no point in arguing, but the vent system regulations are totally over the top.

However, what I am reluctantly coming to understand, is that I have absolutely no choice but to stick two 100mm pipes through the highest point of the roof of the house, with no way to avoid that process?    

Link to comment
Share on other sites

hi ok

             just to put a spanner in the works ..... unless it`s a new build  .. the primary vent is not a part of the " new fosse inspection " only the secondary  vent is ..

                                Dave

Link to comment
Share on other sites

[quote user="DaveandOlive"]

hi ok

             just to put a spanner in the works ..... unless it`s a new build  .. the primary vent is not a part of the " new fosse inspection " only the secondary  vent is ..

                                Dave

[/quote]

Oh, well that's not too bad then. This is a renovation, so I could possibly attach the primary vent into a flush-fitted roof tile outlet on the roof at window-level then?

Thanks again for your help.

Howard.

PS: Why, when I click 'quote' do I get the message "Non matching quote blocks in post" ???

Link to comment
Share on other sites

[quote user="Howie"]PS: Why, when I click 'quote' do I get the message "Non matching quote blocks in post" ???[/quote]Because Dave&Olive's user name contain the character & which the quote facility does not recognise.

I have edited your posts and replaced the & by the word and.

Link to comment
Share on other sites

[quote user="DaveandOlive"]

hi ok

  put it in picture format here a few years ago it may help ....page 5

  http://s83.photobucket.com/albums/j311/daveolive/?start=80

                    Dave

            

[/quote]

Hi again Dave. Thanks for that.

It's really starting to look as though it's going to be simpler getting someone else to do the entire job. By the time I've spent my own time travelling from the UK and bringing or hiring a digger, it looks like it might make more sense.

I'll do a search for installers in my area (56).

Thanks for all your advice.

Howard.

Link to comment
Share on other sites

Can I just ask another quick question regarding toilet vents?

I only have one toilet and I know that it will effectively be the primary vent. But how long can the horizontal waste run from the toilet be, - before I have to put the t-section in to make the vertical vent?

Is there a min/max requirement for this?

Also, can the vent outlet be one of those flush vents that blends in with the roof-tiles?

Thanks again, - in advance.

Howard.

Link to comment
Share on other sites

Please sign in to comment

You will be able to leave a comment after signing in



Sign In Now
 Share

×
×
  • Create New...