I would put it down to low flow rate. The water cools down sufficiently in the rad to create a temperature gradient.

Shut off all the other rads, and see whether this one reaches full temperature. If so, you need to start fiddling with the balancing valves to ensure an as much as possible equal flow through all rads. Can be tricky without specialist kit (basically, the temperature drop across each rad should be similar).

Link to comment
Share on other sites

Probably then corrosion in the bottoms of the castings.

You could try closing them off from the circuit (i.e. capping the feed and return pipes), closing both valves and inserting de-corrosion fluid and leaving for a week or so: and then flushing the rad out.

It would need to be removed and probably inverted.

One danger is if the rad comprises separate sections, then they are joined top and bottom and have gaskets either side of the casting: the gaskets may well leak since they are probably currently sealed by corrosion!

Restorers strip these, dump them in a bath of strong acid (Usually Muriatic I suppose), reverse flush and rebuild, with new gaskets and then sandblast and stove.

See here:

Link to comment
Share on other sites

In a word,  probably no.

Sadly.

If the original pump was properly specified, and the whole system correctly designed, then the pump is really an assist to the natural process of the thermo-cycle.

Unless and accepting if the runs from and to the boiler are excessive, then the system would need some extra "Grunt".

Is the offending rad right at the end of the supply circuit?

Very long pipe runs are usually assisted by installing a secondary pump, at the last rad in circuit.

This is where "Zoning" comes in in design.

How many stories is the house?

Link to comment
Share on other sites

   it is a big house and the runs are quite long but the rad in question is about two thirds of the way down the house,the pump is above the boiler in the cellar at the back of the house.It is only this rad and the next one in line that do not get hot so i guess it is as stated too far away for the pump to get a good flow.
Link to comment
Share on other sites

Well, the first thing to try is "Balancing" the rads.

This is achieved by opening or closing the Lockshield Valves, until the temperature differential of the Flow and Return Pipes is within 20 Deg F.

For a rough rule of thumb, you can reasonably balance the system by closing all rad lockshield valves except the last in circuit; bringing the boiler up to temp: and then gradually opening up the lockshields, backwards, towards the first.

The core concept is the first rad in circuit will receive the hottest water: and the temperature of the circulating water will diminish as it progresses to the last.

In practice, you will find that the first rad will have the valve open a little: and each successive valve will be opened more.

Again, a rule of thumb is to test the temperature of each rad, in an identical place using a surface thermometer.

As a bonus, if the last rad becomes hot top and bottom, when it is the only one in circuit (At the beginning of the test), then clearly it cannot be suffering overmuch from corrosion.

See here:

Link to comment
Share on other sites

I suggest that if you turned all else off and left the suspect rad open, only, and it still refused to reach desired operating temp, then it really is Quad Erat Demonstrandum.

Corrosion.

It is a good idea to replace that rad with a cheap pressed item, perhaps temporarily, both for the Winter and until the defunct unit has been cleansed and restored.

These old cast iron rads are valuable, BTW, so don't be tempted to chuck it![:)]

Link to comment
Share on other sites

Cast Iron rads are just as effective as modern pressed steel items.

Provided the inner corrosion is removed.

They are much slower to reach operating temperature, obviously, since there is a much greater mass of material to heat: but the upside is they are slower to cool down, so are still releasing heat when the CH boiler has shut off.

Different material's efficiency at absorbing and radiating heat, is usually expressed as K (or Thermal Conductivity): additionally," thermal transmittance, incorporates the thermal conductance of a structure along with heat transfer due to convection and radiation.  It is measured in the same units as thermal conductance and is sometimes known as the composite thermal conductance. The term U-value is another synonym."

Cast iron has a K value of 55: whereas copper is 401: and Aluminium 250.

Thus the best rads of all for speedy heat up and heat transfer potential would be copper: not very robust though!

However if one starts at the basic precept that all CH systems are Heat Systems and that radiators are simply Heat Exchangers, then it's all really a matter of Heat In-Heat Out.

If a particular rad is not conducting heat effectively from the water to the air-surface (Where it can then radiate), then the heat of the water in the pipe feed stays very much the same: little difference between the temps of the feed and return.

Thus little energy is lost.

The effectiveness of any radiator is a simple function, really, of its surface area to air. Bigger rad (In area) then bigger potential BTU/Kw heat exchange capacity and thus output to room.

The great benefit of cast iron rads is longevity. There is a much greater thickness of metal to rust through!

And they look great, too.

[:)]