Hi

EDF have just renewed all our old incoming power lines, meter etc, they left two black wires sticking out, and said they were for the chauffe eau, I am assuming these are only live at the time of cheap rate power and can be wired straight into any circuit breaker? Am I correct?

thanks in advance

Link to comment
Share on other sites

They are not live, they are from a volt free or dry relay contact which switches from normally open to closed during the heures creuse, you will need a 2 amp disjoncteur to supply the "asservisement" current through these wires and the realy  contact to your jour/nuit contacteur.

Thes wires will then be carrying a current and should be considered live, until then they are inert and safe.