CeeJay Posted April 15, 2009 Share Posted April 15, 2009 I would like to fit an extractable cooker hood over the hob taking the smells etc via ducting up to the ceiling and venting to an outside wall, even though they are made of large pierres. However I am not sure what the regs. are in France for the wiring. Presumably they can be wired straight from a supply and the hood itself controls the on/off etc. Is there a need to have a connection unit externally or can everything be placed inside the chimney bit? Link to comment Share on other sites More sharing options...
Nick Trollope Posted April 15, 2009 Share Posted April 15, 2009 It should have its own feed from the tableau, protected by a 2A breaker. If the hood will accept the cable directly, then that is fine. No external switch necessary. Link to comment Share on other sites More sharing options...
CeeJay Posted April 15, 2009 Author Share Posted April 15, 2009 Thanks for that Nick, presumably if only a 2amp dis. is required I can wire in 1mm cable? Link to comment Share on other sites More sharing options...
Nick Trollope Posted April 16, 2009 Share Posted April 16, 2009 Yes, if you have it, otherwise use 1,50mm. Link to comment Share on other sites More sharing options...