My house is in the Pyrenees and subsequently can get damned cold in the winter. As I am not there during this period I want to ensure that the heating doesn't freeze up. It is currently fitted with a red anti freeze but I don't know how old this is. Can anyone tell me the name of this in French so I can get some next time I'm down. I can add it to the system myself, no problem. Thanks,

Tony

Link to comment
Share on other sites

Since the present additive efficacy is unknown, as is its composition, I would recommend it is drained (not into the drains). Add the new to the old as a last resort - it should perform OK.

Are you sure there is no drain? Most boilers have a tap right at the bottom, often obscured. Otherwise, crack one of the rad joints?

Suggested products (cheaper in the UK!)

Fernox Alphi 11 (combined inhibitor and anti-gel)

http://www.plumbworld.co.uk/93-770

Sentinel X500 (combined inhibitor and anti-gel)

http://www.gewater.com/applications/sentinel/x500_inf.jsp

Link to comment
Share on other sites

Hi Opel Fruit, absolutely positive that there is no drain off. Have worked with s-plans, y-plans gravity fed etc. in UK,  but there is no drain off. It's a dual gas boiler /storage HW system, Pressurised system. When I first bought the house I assumed that it was like the pressurised  systems in the UK where you take it to 1.5 bar and the secondary system was for HW storage. but as soon as I pressured it, it bled red water via an expansion, as it heated. Found that if I leave the water pressure low the psi gauge rises on warming and , unlike the UK systems it fires without pre-set pressure and no release via the over-pressure.

New to me and worrying as I have to leave it over the winter, hence the anti freeze!

 I can crack a radiator on the lower ground floor  to create an air gap upstairs and carefully drain enough off to introduce the anti freeze on the third floor, then re- pressure, bleed and pump to circulate it. To try and drain it all will be a mule. Then again I have a week with nothing to do but relax, maybe I should drain and  incorporate a drain off at the same time but I dread their poxy micro bore pipework!

Thanks for your input and look forward to more advice.

Tony

Link to comment
Share on other sites

Sealed (pressurised) systems are the norm here. I think you have a problem with the pre-charge in your Expansion Vessel. You should be able to pressurise the system to 1 or 1.2 Bar cold. The pressure read off the manometer should rise as the system heats. You appear to have a problem.

There will be a Schrader valve on the expansion vessel. Whilst the system is partly drained, and thus there is no hydraulic pressure acting on the vessel, I would suggest you use a tyre pressure gauge on the valve to establish whether there is any pre-charge in it. If the pressure is below 1 bar, add air. I would then leave it for a while and re-check to make sure that the vessel is holding air pressure. The air pressure disappears over a few years. The good news is that if the vessel is leaky, you can change it for less than 20 Eur..

French rad piping is normally TBOE, so you may have a blanking plug at the bottom of the rads, which is obviously easy to open for draining. Conversely, you should have an easily removable bleed valve fitment at the top of the rad, so adding Antigel is straightforward. Disturbing pipework is something to avoid if possible.

Adding a drain point is obviously worthwhile, but I would see if it can be done without having to solder anything - water residue will be an issue otherwise.

Commiserations on the microbore.

 